Dorm Rooms

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
No. NEC 210.12 requires AFCI in dwelling units only, and this is not a dwelling unit. 210.18 goes on to require AFCI in dorm rooms that have permanent provisions for cooking, and your building does not.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
No, 210.12 (A) applies to dwelling units and dorm rooms that do not meet the definition of dwelling unit would not require AFCI protection.

Chris
 