A couple days ago we talked about checking conduit size ect on the plans. (can't find thread)
Saw this yesterday, these are plans for a 350 gen. 480/277 from a very good PE.
Note 2 (B): Contractor shall furnish and install separately derived generator grounding system per NEC 250.20(D).
Note 10: New 1000 amp. 277/480 volt, 3 pole, service rated automatic transfer switch with ground fault protection.
These are not in the general notes area but are specific to these plans.
Saw this yesterday, these are plans for a 350 gen. 480/277 from a very good PE.
Note 2 (B): Contractor shall furnish and install separately derived generator grounding system per NEC 250.20(D).
Note 10: New 1000 amp. 277/480 volt, 3 pole, service rated automatic transfer switch with ground fault protection.
These are not in the general notes area but are specific to these plans.