A couple days ago we talked about checking conduit size ect on the plans. (can't find thread)
Saw this yesterday, these are plans for a 350 gen. 480/277 from a very good PE.

Note 2 (B): Contractor shall furnish and install separately derived generator grounding system per NEC 250.20(D).

Note 10: New 1000 amp. 277/480 volt, 3 pole, service rated automatic transfer switch with ground fault protection.

These are not in the general notes area but are specific to these plans.
 
georgestolz said:
I'd submit an RFI, but it appears that the engineer had a lapse in thinking for a moment, these two notes definitely conflict.

I fired off a fax this morning and he got back it was a mistake. I just want to stress how important it is to review all plans. If the EE makes a mistake, the installer should catch it.(or look really incompetent)
 
donny baker said:
Curiously: how did he word the correction?

The way they usually do. Some one that doesn't work there any more drew up the plans and now "I" have it.
These guys a the sharpest EE's I know.(The PE's on this forum are sharper!)
This job was designed for a future larger Gen-Set.(SDS). Just an oversight.
 