Ok, maybe I am a little rusty on electrical theory, but I am trying to wrap my head around what I am witnessing on this generator I am working on.
I was working on reconfiguring a 12 wire 10kw head and on initial startup hoping there was no smoke my amp readings for the windings aren't balanced so I am a bit confused.
10kw 1.0pf resistive load, 240v, 42 amps. The gen head is configured double delta. The gen head is rated at 10kw .8 PF and 52 amps. (MEP-803a for the curious, the work was to remove the commonly failing S8 switch.)

My connections are identical to above. 5 6 7 9 are on N, 8 and 10 are bonded, 2 and 4 are bonded. 1 and 12 is L1 and 3 and 11 are L3.
Amp readings at various points (approximate +/- 1 amp):
L1 - 41 amps
L3 - 41 amps
N - close to nothing
pigtails: I didnt write any of it down, all from memory, I think the 9-12 winding was an amp or 2 more than the 3-6 winding, enough to cause some more heat on the thermal imager but not enough for me to think something was wrong.
3 - 26 amps
12 - 26 amps
11 - 16 amps
1 - 16 amps
8 - 16 amps
2 - 16 amps
So is this normal? I get the basic theory that if you add 2 sinewaves that are 120 out they will match the third so essentially you have 2 sets in parallel. But is this the reason why the load isnt equally split between the pairs of windings? If I had a .8 load at 10kw would the 3-6 and 9-12 windings stay at 26 amps with the other windings increasing to 26 amps or would all of the windings increase proportionately?
I understand (correct me if I am wrong) that normally we de-rate by 1/3 due to circulating currents in this type of configuration. (ill do some more thorough testing today.) But Ive also read contradictory information stating that the amp draw across the single winding would be equal to the amp draw across the dogleg it is paralleled with.
Nameplate on these generators is so conservative that they routinely provide power at 125% for 8+ hours and my readings at 100% is still under the amps limit on the nameplate (52amps, so 26 per winding set) so I am not worried about harming the generator (its standby so added heat contributing to insulation degradation is nil, plus Onan marketed the same engine/genhead combo commercially as a 16kw which I also have one of those. I am just trying to A wrap my head around this and B if theres a problem with this head to know about it. (every set of windings metered at .3 ohms. I didnt meg them.)
I was working on reconfiguring a 12 wire 10kw head and on initial startup hoping there was no smoke my amp readings for the windings aren't balanced so I am a bit confused.
10kw 1.0pf resistive load, 240v, 42 amps. The gen head is configured double delta. The gen head is rated at 10kw .8 PF and 52 amps. (MEP-803a for the curious, the work was to remove the commonly failing S8 switch.)

My connections are identical to above. 5 6 7 9 are on N, 8 and 10 are bonded, 2 and 4 are bonded. 1 and 12 is L1 and 3 and 11 are L3.
Amp readings at various points (approximate +/- 1 amp):
L1 - 41 amps
L3 - 41 amps
N - close to nothing
pigtails: I didnt write any of it down, all from memory, I think the 9-12 winding was an amp or 2 more than the 3-6 winding, enough to cause some more heat on the thermal imager but not enough for me to think something was wrong.
3 - 26 amps
12 - 26 amps
11 - 16 amps
1 - 16 amps
8 - 16 amps
2 - 16 amps
So is this normal? I get the basic theory that if you add 2 sinewaves that are 120 out they will match the third so essentially you have 2 sets in parallel. But is this the reason why the load isnt equally split between the pairs of windings? If I had a .8 load at 10kw would the 3-6 and 9-12 windings stay at 26 amps with the other windings increasing to 26 amps or would all of the windings increase proportionately?
I understand (correct me if I am wrong) that normally we de-rate by 1/3 due to circulating currents in this type of configuration. (ill do some more thorough testing today.) But Ive also read contradictory information stating that the amp draw across the single winding would be equal to the amp draw across the dogleg it is paralleled with.
Nameplate on these generators is so conservative that they routinely provide power at 125% for 8+ hours and my readings at 100% is still under the amps limit on the nameplate (52amps, so 26 per winding set) so I am not worried about harming the generator (its standby so added heat contributing to insulation degradation is nil, plus Onan marketed the same engine/genhead combo commercially as a 16kw which I also have one of those. I am just trying to A wrap my head around this and B if theres a problem with this head to know about it. (every set of windings metered at .3 ohms. I didnt meg them.)