Nietz001
Member
- Location
- St Paul MN
I have a load issue on a large stadium project. The receptacle is approximately 150? from the panel. I pulled in 6 #10?s, (three hots and three neutrals) plus a ground though a ? ? EMT and connected them to a 20 amp breaker. At around 14 amps the breakers trip. The Owner is blaming me but honestly I?m not sure what I could have done differently. Any Ideas?
Would this installation require me to double de-rate? Also, when counting conductors to de-rate does anyone know where in the NEC it tells you to count the neutral as a current carrying conductor?
Any help would be most appreciated.
Would this installation require me to double de-rate? Also, when counting conductors to de-rate does anyone know where in the NEC it tells you to count the neutral as a current carrying conductor?
Any help would be most appreciated.