Double doors

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Below arrangement back to back switchgear seems to comply NEC 2017 110.26(C)(2) but the two doors shown are too close to the switchgear. NEC 2017 110.26(C)(2)(b) has language for the two door locations to be certain distance for switchgear but thats for single door. Their is no such language for two egress.

So would the below arrangement comply per NEC 2017 section 110.26(c)?

c47756528554401a25161c49c9700cc0.jpg
 
Last edited:
110.26(C)(2)(b) addresses clearances with ONE entrance. According to the sketch, you have an entrance at each end so your reference is not applicable, It is compliant,
 