Hello elite engineers,
Recently, I have discussion with my boss about number of services and here is the "brief" contents..
Assuming there is a building with 2-occupancy (not separated by an approved firewall) and they are applying for a service with the utility company. Their service equipment are located in one location and proposing to have an individual service drop coming from a 230V 3-phase transformer bank. They have the same characteristics (voltage, frequency, phase) and the capacity requirements of each occupancy did not exceed 500 amperes each. The service equipments installations are accessible to both occupants.
In my initial analysis, the proposal will result to double service drop and a clear violation of NEC Art. 230.2 Number of Services. This service installation was only permitted when the service is coming from an underground sets of conductors, size 50mm2 and larger, but not connected together at their load end (not parallel conductors), shall be considered to be supplying one service.
1. Was my initial analysis right that this will result to double drop?
2. What is the rational by allowing individual service lateral for each service disconnects not more six and group in one location?
a. Was it considered because there were no service entrance conductors when underground service used (solely served service)?
b. Was it to limit the shorrt-circuit current at the service equipment and permitting lower interrupting capacity-rated equipment?
Thank you
Recently, I have discussion with my boss about number of services and here is the "brief" contents..
Assuming there is a building with 2-occupancy (not separated by an approved firewall) and they are applying for a service with the utility company. Their service equipment are located in one location and proposing to have an individual service drop coming from a 230V 3-phase transformer bank. They have the same characteristics (voltage, frequency, phase) and the capacity requirements of each occupancy did not exceed 500 amperes each. The service equipments installations are accessible to both occupants.
In my initial analysis, the proposal will result to double service drop and a clear violation of NEC Art. 230.2 Number of Services. This service installation was only permitted when the service is coming from an underground sets of conductors, size 50mm2 and larger, but not connected together at their load end (not parallel conductors), shall be considered to be supplying one service.
1. Was my initial analysis right that this will result to double drop?
2. What is the rational by allowing individual service lateral for each service disconnects not more six and group in one location?
a. Was it considered because there were no service entrance conductors when underground service used (solely served service)?
b. Was it to limit the shorrt-circuit current at the service equipment and permitting lower interrupting capacity-rated equipment?
Thank you