Dear all,
I tried to find information that can help me to determine what NEC says about overcurrent protection for equipment connected to wall by plug.
1. Lets say we have table standing machine (used for industry and also laboratory) connected to 1-phase power (phase conductor, grounded neutral conductor and grounding protective conductor) with motor and control circuit inside. Motor is connected to mains by contactor. Machine is connected to wall by plug (Nema 5-15). It is not portable but it can be moved to another place.
Overcurrent protection inside equipment - fuses:
A. One fuse in "hot" line of course according wire ampacity, load, etc..
B. Could there be one separate fuse in L and second in N? Same characteristic, current value, two separate fuse holders, etc. In my opinion NFPA 70 and NFPA 79 says that Grounded conductor (neutral) cannot be disconnected by overcurrent device unless all hot conductors are disconnected simultaneously and this cannot be achieved by two separate fuses? You can say that in case of failure N fuse will blow and hot line will stay intact, therefore it can be dangerous situation mainly for service. But if the equipment is connected to wall by plug how can we be sure that L and N are not swapped before equipment? It is etalon that this cannot happen? Therefore solution with one fuse in hot line could be potential dangerous?
Is there any directive/NEC standard that cover this situation. Fuses in both lines (one phase supply) in equipment connected to wall by plug? Or what NEC say about swapped hot and neutral before equipment and one fuse?
C. To cover all of these issues it seems best solution to use circuit breaker with tight handles for L and N. But I am really interested in fuse solution.
2. Let?s say we have table standing machine (used for industry and also laboratory) connected to 2-phase power (phase conductor L1, phase conductor L2 and grounding protective conductor) with motor and control circuit inside. Motor is connected to mains by contactor. Machine is connected to wall by plug (Nema 6-15). It is not portable but it can be moved to another place.
Same question - how can be overcurrent protection realized? Could this be done only by circuit breaker with tight handles? Or could fuses be anyhow used to do overcurrent protection of this equipment?
I know that I asked a lot of question in this post, but could You be so kind to give me some reasonable answer/link/directive numbers/articles that describing how to proceed with this?
Many thanks
I tried to find information that can help me to determine what NEC says about overcurrent protection for equipment connected to wall by plug.
1. Lets say we have table standing machine (used for industry and also laboratory) connected to 1-phase power (phase conductor, grounded neutral conductor and grounding protective conductor) with motor and control circuit inside. Motor is connected to mains by contactor. Machine is connected to wall by plug (Nema 5-15). It is not portable but it can be moved to another place.
Overcurrent protection inside equipment - fuses:
A. One fuse in "hot" line of course according wire ampacity, load, etc..
B. Could there be one separate fuse in L and second in N? Same characteristic, current value, two separate fuse holders, etc. In my opinion NFPA 70 and NFPA 79 says that Grounded conductor (neutral) cannot be disconnected by overcurrent device unless all hot conductors are disconnected simultaneously and this cannot be achieved by two separate fuses? You can say that in case of failure N fuse will blow and hot line will stay intact, therefore it can be dangerous situation mainly for service. But if the equipment is connected to wall by plug how can we be sure that L and N are not swapped before equipment? It is etalon that this cannot happen? Therefore solution with one fuse in hot line could be potential dangerous?
Is there any directive/NEC standard that cover this situation. Fuses in both lines (one phase supply) in equipment connected to wall by plug? Or what NEC say about swapped hot and neutral before equipment and one fuse?
C. To cover all of these issues it seems best solution to use circuit breaker with tight handles for L and N. But I am really interested in fuse solution.
2. Let?s say we have table standing machine (used for industry and also laboratory) connected to 2-phase power (phase conductor L1, phase conductor L2 and grounding protective conductor) with motor and control circuit inside. Motor is connected to mains by contactor. Machine is connected to wall by plug (Nema 6-15). It is not portable but it can be moved to another place.
Same question - how can be overcurrent protection realized? Could this be done only by circuit breaker with tight handles? Or could fuses be anyhow used to do overcurrent protection of this equipment?
I know that I asked a lot of question in this post, but could You be so kind to give me some reasonable answer/link/directive numbers/articles that describing how to proceed with this?