620.62 does not apply. 620.62 refers to ground faults, and that ground fault protection be coordinated. If there is a fault to ground outside in a landscape light, you won't take out the main breaker of the whole building.
Certain services are required to have Ground Fault Protection on the Main breaker. If so, there is distribution Ground Fault Protection that follows downstream. The coordination is required so that either the Branch Circuit (if present) or the Feeder Ground Fault Protection will trip in a Fault, instead of Higher up the distribuion stream, or even all the way up to the top.
Also, Fusing is not Ground Fault Protection. Fuses act as OverCurrent Protection and Short Circuit Protection. They do NOT sense Faults to ground. Yes, they will or may trip as a result of a fault, only because the resulting current due to the fault may trip the overCurrent Protection, but it is not Fault protection. 620.62 is in regards to FAULTS only.