If I understand your question,

4" square box is not a double gang box. It is a "4 inch square" box

You turn it into a single or double device box by the use of single or double device plaster ring.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If I understand your question,

4" square box is not a double gang box. It is a "4 inch square" box

You turn it into a single or double device box by the use of single or double device plaster ring.


Agreed. If you use a 2 gang ring then it is a 2 gang box. Why does this matter?

352165.png
33a760b3-f72f-44d5-b5ba-4f1ddee3ca22_300.jpg
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It does not matter how you provide the 2 gang. If the plans call for a 2 gang then you need to know the limits of the space and what will wok with the number of conductors. The box you provided a link to can be a 2 gang but I would only use that if I had a fill issue with the number of conductors. Providing a 2 gang IMO only refers to the final outlet space. When a 2 gang is required it is generally to ensure that a specific switch or something similar would fit in it. For instance a 2000 watt dimmer may require a 2 gang box.
 