The electrical grade silica and resin compound completely enclose the coil. There should also be some kind of enamel on the coil themselves right? This initial enamel coating would be the basic insulation, and then the resin compound and silica would be reinforced insulation. Does this sound correct?

Can someone provide an example of a transformer that has conventional double insulation?
 
If you are asking about Class 2 for an Article 725 circuit, those transformers are way too big to have a Class 2 rating.

Sorry...I did not know that Class II = double insulated for a transformer. I don't think I have ever seen one
 
Last edited:
IME double insulated transformers are only readily available in very small sizes such as would be used for 12 volt halogen lamps, for 12 or 24 volt outdoor lighting, and for signalling or bell ringing purposes.

Larger transformers of more than a few hundred VA, as would be installed to use 120 volt equipment from a 480 volt service almost allways have a metal case that requires grounding.
Large transformers generally need a steel case for mechanical strength and fire resistance, and to double insulate this would add appreciably to the cost, weight and bulk of the article.
Also such transformers are almost allways connected to grounded branch circuits, and a ground is also normaly required to the equipment supplied by the transformer, therefore the cost of grounding the transformer case is negligable.
 
"Class II" and "Double Insulated" (same thing by the way) are IEC appliance circuit designations, the Class II is not exactly the same as Class 2 is here in North America. An IEC Class II circuit means that everything in it is double insulated, which means basically that no single failure will result in exposure to live electrical circuits by the user, AND that the devices are used WITHOUT having to have an earthed (grounded) frame. This is as opposed to a Class I circuit that requires earthing and using an RCCD (the equivalent of a GFCI for IEC countries) in the power circuit. Using a Class II transformer is only valid when ALL devices down stream of it are also Class II. In other words the designation is for the CIRCUIT, and to get it, all devices in the circuit must carry the designation, or be of low enough energy to not need it, i.e. battery powered. For that reason alone, Class II tends to only apply to small appliances such as cell phone chargers and other wall warts.

It's unlikely that you will find a transformer of that size with a Class II designation here in North America. Although transformer mfrs here make IEC versions of their products to go on export machinery, attaining something that stringent on a larger transformer would be very expensive and if you don't have enough market demand for it, uncompetitive. If it exists at all (because of how it must be used), only one of the larger IEC mfrs will have it. Then, it's not likely to have a UL listing, if that is going to be necessary as well.
 