could the OP possibly mean--"double lock nuts on each side of the enclosure:jawdrop:
 
Well....Mechanically speaking at any voltage you want as long as you still meet the specific requirements in Section 250.92(as iwire stated in brevity) if dealing with service conductors or Section 250.96 with bonding other enclosures. If you specifically asking "WHERE" they call this out in the NEC then I would direct you to Section 250.97 Ex.(2) which specifically gives some information for bonding over 250 volts.
 
As Bob stated you could use one locknut on the outside and a metallic bushing on the inside.
 