Toros

Senior Member
Location
Tujunga, CA
Hi
is here any 200A double lug
3- phase sud panel
where I can tap off the lug and feed the elevator Thru 150A 3- pole breaker
that is mounted feet away in an enclosure
tanks
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Why the need for Double lugs?

All you need is a panel that accepts a subfeed breaker that size.
 
If you are getting a factory order panelboard, just order one with subfeed or feed through lugs. If its a panel you already have, see if you can swap the lugs out.


ADD: getting a 3 pole 150 amp miniature circuit breaker is going to be expensive, if you can even find it. I would take 6 spaces.
 

Besoeker

Senior Member
Location
UK
Hi
is here any 200A double lug
3- phase sud panel
where I can tap off the lug and feed the elevator Thru 150A 3- pole breaker
that is mounted feet away in an enclosure
tanks
Excuse my ignorance.
What is a double lug panel? Or a single lug for that matter?
 

kwired

Electron manager
Location
NE Nebraska
Replace existing lug with a 2 port lug - some will cry you modified the panel and voided listing though.

Use Polaris (or similar) connecting devices, or even tap devices that don't require cutting the conductor you are tapping, presuming you have the space to use them.

Use a 400 amp panel- it probably has main lugs that accept one or two conductors, might not be that much more then if you used the polaris connectors and a 200 amp panel.

This all assuming you are dealing with a 200 amp feeder and a main lug panel, which I think you were.

someone already mentioned feed thru/sub feed lug options.
 