:roll: This is a question that is a follow up to a earlier post on transformer protection (primary and secondary) Knowing that you cannot tap a transformer secondary conductor, does this mean that if you were to feed a 225A panelboard with a MCB (within 10?-0) that if that panelboard was specified or supplied with double lugs then the feeder from the set of double lugs to the adjacent panelboard would be a code violation because of no over current protection correct? For sub-feed or feed-thru lugs you would still be protected by the original panel MCB but this is not the case with double lugs. Is this line of thinking correct or am I way off base?? Thanks in advance for your thoughts.