J jonny1982 Member Location CA Jan 23, 2020 #1 By NEC code, can a single mc cable be installed in a double mc connector? Or a single mc cable in a double mc cable to 3/4" EMT changeover fitting? Thanks.
By NEC code, can a single mc cable be installed in a double mc connector? Or a single mc cable in a double mc cable to 3/4" EMT changeover fitting? Thanks.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jan 23, 2020 #2 It depends on the listing of the connector. The connector instructions would say something like suitable for use with one or two cables.
It depends on the listing of the connector. The connector instructions would say something like suitable for use with one or two cables.
Knuckle Dragger Master Electrician Electrical Contractor 01752 Location Marlborough, Massachusetts USA Occupation Electrical Contractor Jan 23, 2020 #3 I don't know for sure but I do it whenever I feel I may be adding an additional circuit in the near future.
I don't know for sure but I do it whenever I feel I may be adding an additional circuit in the near future.