I have a double oven that has a nameplate rating of 7.4KW
There is a 10-3 on a 30 amp breaker run to it. Can I go off of column B and size the circuit at 80% of 7.4 KW? Is the 30 amp circuit okay?
Table 220.55 is for demand factors and loads, that is for service load calculations. For branch circuit load you need to look at note 4 of the table.
Does the nameplate cover both ovens, or does each oven have a nameplate?
Table 220.55 is for demand factors and loads, that is for service load calculations. For branch circuit load you need to look at note 4 of the table.
Does the nameplate cover both ovens, or does each oven have a nameplate?
I disagree that the table is for service calculations only. If so you would not be able to use the Notes and the Notes take us back to the Table.
IMO, if you have a double oven then you would do as the op stated. Take the 7.4kw and use column B. So 7400 * .8= 5920 watts. Divide by 240 and you have 25 amps. I believe the 10/3 would work but I am not sure I would use #10. The ovens have t-stats so the loads generally won't be on at the same time for long periods. Even if they are the load is just over 30 amps with no demand and that is not likely to trip the breaker.
I guess it depends if you see this as one oven or two ovens. If it is one oven then I guess a 40 amp circuit is needed.
Dennis, what about Note 4 to 220.55. Would that not direct us for one wall mounted oven, the branch circuit shall be the nameplate rating ?
I disagree that the table is for service calculations only. If so you would not be able to use the Notes and the Notes take us back to the Table.
IMO, if you have a double oven then you would do as the op stated. Take the 7.4kw and use column B. So 7400 * .8= 5920 watts. Divide by 240 and you have 25 amps. I believe the 10/3 would work but I am not sure I would use #10. The ovens have t-stats so the loads generally won't be on at the same time for long periods. Even if they are the load is just over 30 amps with no demand and that is not likely to trip the breaker.
I guess it depends if you see this as one oven or two ovens. If it is one oven then I guess a 40 amp circuit is needed.