Originally posted by charlie:
Sorry but 240.20(B) requires a circuit breaker to open all ungrounded conductors of the circuit both manually and automatically unless otherwise permitted in 240.20(B)(1), (B)(2), and (B)(3). This was changed by panel 10 in the 2005 cycle to require a common trip mechanism. If the 2005 Code has not been adopted in your area, you may still use single pole circuit breakers with approved handle ties.![]()