Can a double pole breaker be used as a single pole breaker? I have a 3 pump control panel that is 120V single phase 39 FLA. Do they make a 40 or 50 amp single pole breaker? Thanks
Some breakers with external handle ties also include an internal tie, so they are always 'common trip'.Yes you can use only one pole. Although it's not required, when I do this I pull the handle tie off. (mainly because I might need it later......Also to avoid confusion and proper panel labeling. One marked spared and othe marked with the proper equipment name.
Some breakers with external handle ties also include an internal tie, so they are always 'common trip'.
But this got me to thinking, Do you think if they were common trip internally, could you load one at 2 amps and one at 15 without causing a problem? Would this "confuse" the breaker,,,,,so to speak?
The handle is for simultaneous operation. 2-pole breakers will trip both poles if only one is overloaded, even if you remove the handle tie.Some breakers with external handle ties also include an internal tie, so they are always 'common trip'.
They are indeed simply two 1-pole cases riveted together, but there is a link between the cases that assures simultaneous tripping, again, even without the handle tie.Good point, I was picturing the cheap, two single poles, riveted together one.
Nope. Each breaker pole acts as a breaker for that line. The internal common trip means that the overloaded pole will take out the other(s) when it trips.But this got me to thinking, Do you think if they were common trip internally, could you load one at 2 amps and one at 15 without causing a problem? Would this "confuse" the breaker,,,,,so to speak?