Basically 30 amp and less "standard" 1 through 3 pole QO breakers that have the pressure plate design terminals are listed for one or two conductors, I believe 14-10 AWG. They typically accept up to 8 AWG but I think only one conductor is mentioned for 8 AWG.
GFCI, AFCI breakers have the pressure plate design, but the case is molded so that one side isn't accessible and therefore they are rated for only single conductor per terminal.
Breakers over 30 amps don't have the pressure plate type terminals and are only rated for a single conductor, same goes for tandem breakers.
I have seen older 15-30 amp breakers with a different termination style that only accepted single conductor, but they have been using the current termination style with very minimal changes for at least 40-50 years now.
I think you will find about the same things for the Homeline series.
GFCI, AFCI breakers have the pressure plate design, but the case is molded so that one side isn't accessible and therefore they are rated for only single conductor per terminal.
Breakers over 30 amps don't have the pressure plate type terminals and are only rated for a single conductor, same goes for tandem breakers.
I have seen older 15-30 amp breakers with a different termination style that only accepted single conductor, but they have been using the current termination style with very minimal changes for at least 40-50 years now.
I think you will find about the same things for the Homeline series.