Have a customer with a new property who wants a 200A service installed on the well house with panel inside, to run the water, trailer recep, and constuction power. No probs.
Question is, when it comes time to use the same service to power the house after it is built. Can the meter-base load-side lugs be tapped again, eg. with those vinyl-covered triple-tap Polaris splices?
Or should I use a 200A-rated feed-through panel in the well house now and plan on going that way later to power the house?
Or some additional dedicated tap enclosure for both (ugly) ?