I have a 45kVA 600-480/277V step down transformer I'm using for a Canadian job. I typically have one transformer feed one load, but here I have two 480V loads with integral CBs in the same small room of the transformer. I would like to bring two sets of wires from the transformer, one to each of these loads (a panel and a piece of equipment). Each load has its own integral CB. Reading 240.21 is making me crossed eyes and I'm not clear if this is technically a 'tap' or not. I would size each set of conductors based on the equipment it's feeding. Any help if this is permitted? Thanks!
 
Hello,
I have a 45kVA 600-480/277V step down transformer I'm using for a Canadian job. I typically have one transformer feed one load, but here I have two 480V loads with integral CBs in the same small room of the transformer. I would like to bring two sets of wires from the transformer, one to each of these loads (a panel and a piece of equipment). Each load has its own integral CB. Reading 240.21 is making me crossed eyes and I'm not clear if this is technically a 'tap' or not. I would size each set of conductors based on the equipment it's feeding. Any help if this is permitted? Thanks!

Under the NEC, you can run individual sets of conductors to multiple loads from the secondary of a transformer. Each set must comply with the requirements of 240.21(C). Also, the transformer protection must comply with 450.3(B).

(I don't know what the Canadian code would require.)
 