DallasDave
New User
- Location
- Dallas Texas
- Occupation
- Retired
In my Challenger service panel (no shutoff before it), the neutral bar and the ground bar are bonded under a plastic cover piece behind the main shutoff.
The ground bar allows for double-tapped EGCs.
I have 5 double-tapped neutrals that I want to take back to a single wire per lug to conform to NEC 408.41 Grounded Conductor Terminations.
I have 5 open lugs on my ground bar, 2 on the top and 3 at the bottom.
Can I put the 5 double-tapped neutrals on the ground bar or is that not permitted by NEC 200.2 (B) Continuity ?
If not permitted, what to do ?
Thanks so much.