Double tapped

Status
Not open for further replies.

Tony P.

Member
Location
Arizona
Occupation
Industrial Refrigeration Engineering
The code mentions double tapped neutrals being not allowed, but the why is missing. In the breaker panels exist terminal strips for landing wiring neutrals and grounds. If we have more neutral and/or ground wire conductors than we have terminal positions, what is acceptable remedy?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
By double tapped you are referring to only one neural conductor under a terminal?
It was long a UL requirement before being added to the NEC, if you don't get this correct you will let the smoke out
First this is the correct way 1618948601211.png
 

Tony P.

Member
Location
Arizona
Occupation
Industrial Refrigeration Engineering
Tom baker,
Yes, the issue is two (2) wires going to the neutral or ground buss terminals. I get the electronics of the lifted neutral, just do not follow the why of only one wire per screw terminal. In my experience, albeit not a total experience like folks who do this everyday, all day, if the connections are made properly then they don’t loosen up.
Is the EGC bar an adder to increase terminals count?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The answer is in the hands of a NRTL not the NEC, the NEC is basically just enforcing the listing of the equipment. Besides that, loosening a double tapped egc screw will not cause the same problem as loosening a double tapped neutral screw when both are carrying a load

Roger
 
Last edited:

Tony P.

Member
Location
Arizona
Occupation
Industrial Refrigeration Engineering
Roger,
What or who is NRTL?
Also, do you have a pix of EGC terminal?
I’m not familiar with those terms.
Thnx.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
NRTL stands for "National Recognized Testing Lab" such as UL for instance. I may be wrong but I think most neutral/ground bars are listed for one grounded conductor per terminal.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes the neutral bar is listed for only one neutral conductor per hole and has been listed that way for decades. The NEC added to wording directly into the code because very few knew about the listing of the neutral bar.
 

Tony P.

Member
Location
Arizona
Occupation
Industrial Refrigeration Engineering
Guys,
Thanks for the help. I’ll look into adder terminals. The fun that comes with a house panel that wasn’t wired by the code standards. Fear not, I going to fix it!
 