tonype
Senior Member
- Location
- New Jersey
Nope. Look at the sticker on the breaker, it does not list any combinations of wires, only a range for one.
I doubt the neutral and ground lugs are listed for two wires either, if they were, they will be stamped or marked.
Is this under the "LUGS CU-AL" portion?
Yes. Some breakers allow the lugs to be changed, but that one does not look like it.
I agree too. Write it up along with the neutrals and GEC's to the left in the photo.
What it is saying below that is that the lugs are rated for 2/0 to 250 conductors, aluminum or copper.Is this under the "LUGS CU-AL" portion?