jwatts
Member
- Location
- Chicago, IL
Inspector told me he was Ok with pulling a #10 neutral for the range circuit if I could show him the exception in the code. After looking at 210.19(A)3 exception 2, that there are instances where you can downsize the neutral. However Im a bit confused on calculating the load. Do i just take 70% of the branch circuit rating? Meaning 40amps x.70=28amps? The reference to table 220.55 is what is throwing me off. The ranges are all single phase 208v on the MDU project. This inspector wants me to show him the math on any type of exceptions to the code, so I would like know if my calculations are correct before showing him.