Whatsup with the whole downsizing the neutral on a service 200 amp gets 2ot 2ot 1ot 2 hots and 1ot neutral guys tell me not to do this just up the neutral to 2ot can you guys (my trusted elders) point me to a reference in the nec that clarifies this for me so im doing what the code says any thoughts on this will be great aswell thanks!
220.61 Feeder or Service Neutral Load.
(A) Basic Calculation. The feeder or service neutral load
shall be the maximum unbalance of the load determined by
this article. The maximum unbalanced load shall be the
maximum net calculated load between the neutral conductor
and any one ungrounded conductor.
Exception: For 3-wire, 2-phase or 5-wire, 2-phase systems,
the maximum unbalanced load shall be the maximum
net calculated load between the neutral conductor and any
one ungrounded conductor multiplied by 140 percent.
(B) Permitted Reductions. A service or feeder supplying
the following loads shall be permitted to have an additional
demand factor of 70 percent applied to the amount in
220.61(B)(1) or portion of the amount in 220.61(B)(2) determined
by the basic calculation:
(1) A feeder or service supplying household electric
ranges, wall-mounted ovens, counter-mounted cooking
units, and electric dryers, where the maximum unbalanced
load has been determined in accordance with
Table 220.55 for ranges and Table 220.54 for dryers
(2) That portion of the unbalanced load in excess of 200 amperes
where the feeder or service is supplied from a
3-wire dc or single-phase ac system; or a 4-wire, 3-phase,
3-wire, 2-phase system; or a 5-wire, 2-phase system