C Clawrence New User Location Cincinnati Occupation Electrician Mar 17, 2025 #1 I got 6’s feeding a 60 amp disconnect, am I able to downsize to 10’s or even 12’s if the motor I’m wiring up only pulls 10-11 amps?
I got 6’s feeding a 60 amp disconnect, am I able to downsize to 10’s or even 12’s if the motor I’m wiring up only pulls 10-11 amps?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 17, 2025 #2 The motor conductors are sized at a minimum of 125% of the FLC jn Article 430. The OCPD can be larger than the rating of the conductors but more info is required. 60 amps for a 10 amp motor load is likely too large.
The motor conductors are sized at a minimum of 125% of the FLC jn Article 430. The OCPD can be larger than the rating of the conductors but more info is required. 60 amps for a 10 amp motor load is likely too large.
R retirede Senior Member Location Illinois Mar 17, 2025 #3 If the OCPD is the same as the disconnect (60A), I agree with Infinity.