Hi All, I have a 75KVA 480-240/120 center tapped transformer. Do I need to have 4 Wire panel at its downstream where center tap will act as a neutral?
Thanks
Thanks
Hi All, I have a 75KVA 480-240/120 center tapped transformer. Do I need to have 4 Wire panel at its downstream where center tap will act as a neutral?
Required for service but not for separately derived system.... which of course means there will be no line-to-neutral loads.AFAIK you need to bring the grounded conductor to the first disconnecting means...
I have 3-phase, 240V load only. Can i just ignore the center tap and just use 3 wires on secondary like a delta only?
You have to bring a grounded conductor to first disconnect, whether it be a neutral conductor or a grounded phase conductor, or is just used as an equipment grounding conductor. If EGC only it can be qualifying metal raceway, cable sheath or other wiring method, plus EGC still needs extended (wiring method again acceptable) to nearly everywhere in the system.Required for service but not for separately derived system.... which of course means there will be no line-to-neutral loads.
The center tap is typically required to be grounded (depending on loads) whether neutral is run or not. System bonding jumper and GEC can be connected at first disconnecting means if the neutral is run.
Grounded does not equal grounding.You have to bring a grounded conductor to first disconnect, whether it be a neutral conductor or a grounded phase conductor, or is just used as an equipment grounding conductor. ...
I know, should have worded it differently. He still needs a conductor where he is asking about - unless the wiring method itself is a qualifying EGC. If he has 120 volt loads to supply he needs two conductors (most instances) where he is asking about.Grounded does not equal grounding.