I have the following scenarios:

1. I have 1000 amp breaker and downstream panelboard is 800A

2. I have 1200A breaker in switchboard and downstream ATS is 800A

#1 is about panleboard and #2 is about ATs. Would the above be acceptable by NEC 2014? If not then which section(s) is not in compliance?
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have the following scenarios:

1. I have 1000 amp breaker and downstream panelboard is 800A

2. I have 1200A breaker in switchboard and downstream ATS is 800A

#1 is about panleboard and #2 is about ATs. Would the above be acceptable by NEC 2014? If not then which section(s) is not in compliance?

Like to add #1 panelboard is MLO
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
If this is a test question please tell us what you think the answer is first.

;)
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
If this is a test question please tell us what you think the answer is first.

;)

Ha! This is whats shown on plans. I gave comments breakers won’t protect downstream equipment. I got response back Breakers are series rated with equipment where is it in NEC 2014. Cannot enforce. Looked but did not find

Please
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Ha! This is whats shown on plans. I gave comments breakers won’t protect downstream equipment. I got response back Breakers are series rated with equipment where is it in NEC 2014. Cannot enforce. Looked but did not find

Please
Here’s something on series ratings


 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Here’s something on series ratings



Ok But the questions post #1 has nothing to do with series rating. Thats response I got from engineer. I know engineer who did plans is confused.

Where is it in NEC 2014 that if upstream breaker is rated at 1000A trip and downstream panelboard bus is 800A MLO then it wont protect the panelboard? Similar question for ATS post #1
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Do you actually look at the NEC before you ask :)
#1 408.36 MLO would be a violation.
#2 Depends on the ATS having an internal line breaker .
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Yea, series rating has nothing to do with it.

A 1000A breaker does not protect an 800A panelboard from overload. However the install may be compliant if other aspects of the system provide the necessary protection.

For example the load breakers in the panel might prevent overload. I don't know the details so can't comment on specifics.

Same with the ATS. The upstream breaker is not protecting the ATS from overload but other aspects of the system may make it a compliant install.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
#1 Not compliant. Panelboard must be protected within it's rating. See Art. 408.
#2 Not compliant. ATS must be protected per it's listing. This will be a very specific list of breaker models and sizes.
 