andy s. said:
ROTFLMAO when I saw that the line had the hot and neutral attached to the DPST switch. From the switch, the motor and receptacle are attached, thus breaking both the hot and the neutral.
No need to laugh there is nothing wrong with that and if they sell that unit in a country that does not use a grounded conductor it will be fine there as well.
First lets start by call the conductors by the proper names.
What you called 'Hot' is the
ungrounded conductor.
What you called 'Neutral' (It's not) is the ground
ed conductor.
And what you called 'ground' is the ground
ing conductor.
Fortunately the ground is attached to the housing.
That is all that really matters.
My quandry is, in event of this device being accidentally wetted, (wet/dry vac) would this provide a greater potential for shock hazard,
No.
As long as the ungrounded conductor is switched with the grounded conductor there is no problem at all.
not to mention if this was on a GFCI circuit, how would this come to be if the GFCI senses the difference in potential.
The GFCI will work fine, all the GFCI senses is the amount of current on the two circuit conductors, if the current is different by more than 6 or 8 ma the GFCI will operate.
And how would this be applicable to AFCI.
The AFCI will not 'know' the difference either.
I tried it on AFCI while slowly trying to toggle (very slowly) and my results were rather odd. Sometimes it would trip and sometimes not.
Try the same test with the neutral spliced through solid and I bet you get the same random results.
Come on folks! What's your input. IMHO, I feel that this may be a good sticking point for a change. I like to keep the neutrals tied together.
I don't see any need for a change, there is no safety issue as long as both circuit conductors are switched together.
Their response was, since the plug was not polarized, and the motor being universal, that's the way they do things, because of the nature of the beast, these guys (the consumer) loves pulling that ground off and the potential of flipping the plug,
Well that does happen and by switching both conductors they guarantee that the neutral will not be switched separately if the cord is supplied reverse polarity.
So if that is the reason they did it I say good thinking on their part.