Drain pumps in exam rooms in obgyn

Purr24

Member
Location
Pennsylvania
Occupation
Electrician
Does a drain pump GFCI receptacle need to be wired with HCF cable in exam rooms? This receptacle is in a cabinet under the sink.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
IMO it does.
See the definition of "Patient Care Vicinity" and "Patient Bed Location." (take note of Procedure Table) Even though the receptacle may be under a cabinet the equipment that may come in contact with the patient doesn't care. IOWs, 517.13 (A) & (B) are applicable.
 