Looking for examples on how to represent a draw out circuit breaker in the drawn-out position on a PC interface HMI. Thanks in advance.
Option 1 is good for showing a racked out breaker.___<<---[cb}--->>
---|________________|---
This is option 2
That's basically how i do it....The Russelectric HMI we've inherited at one of our data centers uses a solid box (red = closed, green = open) for a racked-in breaker, and an outline for one that's been drawn out. I found this example with a quick Google.
Appreciate the input, I also found that early on, but that doesn't satisfy the objective. The idea for this HMI is to avoid excessive use of color, saving it only for alarms and abnormal status indications. I referenced that in an early reply but should have stated it in the original post.The Russelectric HMI we've inherited at one of our data centers uses a solid box (red = closed, green = open) for a racked-in breaker, and an outline for one that's been drawn out. I found this example with a quick Google.