Attached drawing, study it carefully. It is just a generic drawing and is just to show a concept.
However, this circuit is from a real machine and I wonder if this is in violation.
My concern is with them using the main OCPD for the VFD and also tapping the other motor and control XFMR from the downstream side of that same OCPD. Which is BTW a J-class fused disconnect.
Couldn't attach a PDF so I made it an image..
However, this circuit is from a real machine and I wonder if this is in violation.
My concern is with them using the main OCPD for the VFD and also tapping the other motor and control XFMR from the downstream side of that same OCPD. Which is BTW a J-class fused disconnect.
Couldn't attach a PDF so I made it an image..