Where in the code (250) does it require bonding/grounding connections to be drilled and tapped? Also where is indicated in (250) that a ground screw must be green?
 
Zane Bailey said:
Where in the code (250) does it require bonding/grounding connections to be drilled and tapped? Also where is indicated in (250) that a ground screw must be green?
It is my understanding that a ground screw cannot be a sheetmetal screw It however can be a sheetrock screw as far as I know.
 
Zane Bailey said:
Where in the code (250) does it require bonding/grounding connections to be drilled and tapped? Also where is indicated in (250) that a ground screw must be green?
First Q...
2008 NEC
250.8 Connection of Grounding and Bonding
Equipment.​

(A) Permitted Methods. Grounding conductors and bonding jumpers shall be connected by one of the following means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less than two threads in the enclosure

(7) Connections that are part of a listed assembly
(8) Other listed means​
(B) Methods Not Permitted. Connection devices or fittings that depend solely on solder shall not be used.​
 
Zane Bailey said:
Where in the code (250) does it require bonding/grounding connections to be drilled and tapped? Also where is indicated in (250) that a ground screw must be green?

250.8.....if 2008 (changes this cycle) Lists the permitted methods.

No mention of green......Myth?

10-32 macine screw for me. The green screws you buy will be a 10-32

I drill and tap the hole with a combo drill tap bit.
 
Zane Bailey said:
Also where is indicated in (250) that a ground screw must be green?

The only 'ground screw' that is NEC required to be green is the grounding screw on a wiring device like a switch, receptacle, cord cap etc.

See 250.126 for that requirement.

There is no requirement that the screw used to attach an EGC to an enclosure be green.
 
I keep 10/32 GND screws in my brief case, always come in handy for that missing dead front cover screw. The hex head works great and perfect length.
 
iwire said:
The only 'ground screw' that is NEC required to be green is the grounding screw on a wiring device like a switch, receptacle, cord cap etc.

See 250.126 for that requirement.

There is no requirement that the screw used to attach an EGC to an enclosure be green.

The only other place besides the "only place" as quoted above is 250.28 (B), but that isn't for "ground screws" , it is the main bonding jumper screw requirement if screw is used for that.
 
frizbeedog said:
250.8.....if 2008 (changes this cycle) Lists the permitted methods.

No mention of green......Myth?

10-32 macine screw for me. The green screws you buy will be a 10-32

I drill and tap the hole with a combo drill tap bit.

Whatever you decide to use, don't 'run em home' with a power tool!