mshields
Senior Member
- Location
- Boston, MA
drip pan over electrical panels.
Article 110, 6 foot clearance, 25 foot clearance rules notwithstanding; in an existing installation, we are trying to persuade an electrical inspector to allow the installation of a panelboard above which at about 5 feet is a water pipe. As we don't have a lot of options, we are proposing a drip pan with drain in the corner such that water would just drip directly onto the floor.
So, I'm thinking of a typical galvanized steel drip pan but he asked for specific specifications, don't know if he'll insist on it, but a detail would be stupendous. I used to have such a thing but cannot find. Does anyone have such a detail and would you be willing to share it with me.
A specification would suffice.
Much appreciated,
Mike
Article 110, 6 foot clearance, 25 foot clearance rules notwithstanding; in an existing installation, we are trying to persuade an electrical inspector to allow the installation of a panelboard above which at about 5 feet is a water pipe. As we don't have a lot of options, we are proposing a drip pan with drain in the corner such that water would just drip directly onto the floor.
So, I'm thinking of a typical galvanized steel drip pan but he asked for specific specifications, don't know if he'll insist on it, but a detail would be stupendous. I used to have such a thing but cannot find. Does anyone have such a detail and would you be willing to share it with me.
A specification would suffice.
Much appreciated,
Mike
Last edited by a moderator: