I'm filing an electrical service that is greater than 1000kVA. The electrical equipment (switchboard) is going to be below the plumbing pipes, but the pipes are above the 6ft of required dedicated electrical space. So I proposed a drip pan to protect the equipment to comply with 110.26(F)(1)(b)
The plan examiner reviewed my the plans and also spoke with the commissioner who is above him. The plan examiner stated that DOB is not allowing drip pans above electrical equipment even though I have informed him that the drip pans and pipes are above the 6ft dedicated space.
Am I missing something? Installing drip pans is common practice, how is this not allowed??? Why am I being told this now because I could not find anything in writing stating this was not allowed prior to design.
This is an existing building, and there is no room for the panels because of the pipes. At this point I'm blind folded and hands tied behind my back. I don't know what to do.
The plan examiner reviewed my the plans and also spoke with the commissioner who is above him. The plan examiner stated that DOB is not allowing drip pans above electrical equipment even though I have informed him that the drip pans and pipes are above the 6ft dedicated space.
Am I missing something? Installing drip pans is common practice, how is this not allowed??? Why am I being told this now because I could not find anything in writing stating this was not allowed prior to design.
This is an existing building, and there is no room for the panels because of the pipes. At this point I'm blind folded and hands tied behind my back. I don't know what to do.