Lets discuss drip pans and sprinkler pipes, please.
I have two concerns.
110.26(F)(1)(c) states:
(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
Other piping discussed in that section requires drip pans. Does the second part of (c), where the piping complies with this section, mean that the sprinkler piping must also have drip pans ? Would a pan under a sprinkler head not deflect heat and delay operation ?
Secondly, in my particular application I have piping (various) over a 12kv/480 unit substation (transformers/breakers/monitoring etc all in one cabinet). Since a portion of this is > 600v I checked 110.34(F) which addresses foreign piping.
The following wording appears:
............Protection shall be provided where necessary to avoid damage from condensation leaks and breaks in such foreign systems. Piping and other facilities shall not be considered foreign if provided for fire protection of the electrical installation.
so, in that section, it appears the sprinkler piping is not " foreign" and requires no protection.
I am confused in that one Code section applicable to my install seems to indicate drip pans under my sprinkler pipes whereas another does not.
Input appreciated.
I have two concerns.
110.26(F)(1)(c) states:
(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
Other piping discussed in that section requires drip pans. Does the second part of (c), where the piping complies with this section, mean that the sprinkler piping must also have drip pans ? Would a pan under a sprinkler head not deflect heat and delay operation ?
Secondly, in my particular application I have piping (various) over a 12kv/480 unit substation (transformers/breakers/monitoring etc all in one cabinet). Since a portion of this is > 600v I checked 110.34(F) which addresses foreign piping.
The following wording appears:
............Protection shall be provided where necessary to avoid damage from condensation leaks and breaks in such foreign systems. Piping and other facilities shall not be considered foreign if provided for fire protection of the electrical installation.
so, in that section, it appears the sprinkler piping is not " foreign" and requires no protection.
I am confused in that one Code section applicable to my install seems to indicate drip pans under my sprinkler pipes whereas another does not.
Input appreciated.