Many years ago when we installed VFDs, we often used a drive isolation transformer. For the last 15 years or so, we have not being doing that.
I am looking at installing a 600 hp, 460 volt drive that will be supplied from a 2500kVA transformer in an industrial facility.. Most of the other load is across the line start motors with a few smaller VFDs and a couple of lighting transformers.
Is there any need for a drive isolation transformer or a line side reactor for this installation?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If your source kVA is more than 10x the drive kVA, you absolutely want at least a line reactor.

DITs in the “olden days” were necessary to decouple the line notching caused by SCR voltage control front ends on the old 6 step inverters. The advent of diode front ends on voltage source PWM drives did away with that need.

A DIT is only necessary now if you have a DC drive, or to deal with a delta source. PWM VFDs are not designed for delta sources, the components are generally selected for Wye, where the voltage reference to ground is lower. The DIT will always be a Wye secondary. But if you do use a DIT, you don’t need the line reactor, it will serve that function too.
 

JoeStillman

Senior Member
Location
West Chester, PA
Some drives have an internal zig-zag transformer to make it twelve-pulse. They're much better for harmonics. I wouldn't put a DIT upstream of that.

Jraef, did you mean less than 10x drive kVA? A stiffer source would be more immune to noise. His 600HP on a 2500 kVA is going to be way more than 1/10 in load / source. I would definitely specify reactors for that.
 