Ok, Section 430.3 says a transformer has to be protected at 125% of the rated current. 430.52 says a motor can be protected at 250% of rated current. If I'm simply trying to provide isolation, it seems I'm being forced to over-size my transformer just to meet the 430.3 protection requirements.
Looks like I have to put a 51kVA transformer ahead of a 15HP VFD, or else use a motor branch circuit protection of only 125% of FLC. What am I missing?
Looks like I have to put a 51kVA transformer ahead of a 15HP VFD, or else use a motor branch circuit protection of only 125% of FLC. What am I missing?