Has anyone heard of an inspector wanting a separate drop ceiling inspection.
The way Ive always done it is to run a whip and come back after tiles are up.

This is for finishing a basement.
 

RICK NAPIER

Senior Member
Location
New Jersey
Yes it is common. We are both from NJ and I always see it required particularly on commercial sites and for all fields with work above the ceiling.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
commonplace here... inspect ceiling after fixtures have been supported & wired before tiles are in place.
 

jwjrw

Senior Member
Yep same here call a wall rough in then a ceiling then a final. Oops forgot the csst bonding rough and final they require here...
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The same here, all items will be in place and inspected before tiles are dropped in. Sometimes borders are allowed to be installed before the overhead inspection but, that would be coordinated with the inspector.

Roger
 
Last edited:

iwire

Moderator
Staff member
Location
Massachusetts
The same here, all items will be in place and inspected before tiles are dropped in. Sometimes borders are allowed to be installed before the overhead inspection but, that would be coordinated with the inspector.

Roger

Exactly the same here, often we can allow 'the cuts' to be put in place but all full tiles remain out until the ceiling inspection.
 

fishin' electrician

Senior Member
Location
Connecticut
Need an above ceiling inspection in CT. They will make you remove the tiles, and I mean all of them, except cut tiles around the perimeter and of course any tiles that have fixtures, devices, etc in them. Meaning the inspector won't just pop his head through one and look around with a flashlight.
 

nyerinfl

Senior Member
Location
Broward Co.
If you are doing CAT5 cabling say in an office space in addition to the electric, you should have that above ceiling inspection as well at the same time if possible as it could also prevent the closing of the ceiling.
 

rodneee

Senior Member
i could not tell you what code and when, but it seems like we never had ceiling inspections until they started to require wire strap supports for the layins. now every ceiling gets inspected.
 

btharmy

Senior Member
Location
Indiana
Have it here too. Some inspectors don't like ladders and make clear up front, NO tiles till inspection. One G.C. tried to get away with leaving tiles out every 10 tiles in a grid pattern. No dice. Inspector said to call him back for re-inspect when tiles were removed, all of them, including cuts. It was a large big name kids pizza place/arcade. Lots of tiles.
 