I am designing a building for a sheltered workshop. Their existing building has drop cords from the ceiling and they would like the new building to have the same. ButI don't think the code will allow it now.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Re: drop cords from the ceiling.

As long as the cords do not go through a ceiling, they should be allowed.

210.50(A), 400.7(A)(1), and 314.23(H)(1) all allow cord pendants.
 

straps

Senior Member
Re: drop cords from the ceiling.

Just install strain relief fittings at the boxes.
Good luck with your people they are special
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: drop cords from the ceiling.

Originally posted by straps:
Just install strain relief fittings at the boxes.
Good luck with your people they are special
Yes strain reliefs but you must also use boxes with threaded hubs.

Forget about 4" squares hanging by cord.
 