K K_Mark Member Sep 7, 2005 #1 I am designing a building for a sheltered workshop. Their existing building has drop cords from the ceiling and they would like the new building to have the same. ButI don't think the code will allow it now.
I am designing a building for a sheltered workshop. Their existing building has drop cords from the ceiling and they would like the new building to have the same. ButI don't think the code will allow it now.
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Sep 7, 2005 #2 Re: drop cords from the ceiling. why wouldn't it?
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Sep 7, 2005 #3 Re: drop cords from the ceiling. As long as the cords do not go through a ceiling, they should be allowed. 210.50(A), 400.7(A)(1), and 314.23(H)(1) all allow cord pendants.
Re: drop cords from the ceiling. As long as the cords do not go through a ceiling, they should be allowed. 210.50(A), 400.7(A)(1), and 314.23(H)(1) all allow cord pendants.
S straps Senior Member Sep 7, 2005 #4 Re: drop cords from the ceiling. Just install strain relief fittings at the boxes. Good luck with your people they are special
Re: drop cords from the ceiling. Just install strain relief fittings at the boxes. Good luck with your people they are special
iwire Moderator Staff member Location Massachusetts Sep 7, 2005 #5 Re: drop cords from the ceiling. Originally posted by straps: Just install strain relief fittings at the boxes. Good luck with your people they are special Click to expand... Yes strain reliefs but you must also use boxes with threaded hubs. Forget about 4" squares hanging by cord.
Re: drop cords from the ceiling. Originally posted by straps: Just install strain relief fittings at the boxes. Good luck with your people they are special Click to expand... Yes strain reliefs but you must also use boxes with threaded hubs. Forget about 4" squares hanging by cord.
B benaround Senior Member Location Arizona Sep 7, 2005 #7 Re: drop cords from the ceiling. 406.4??????? 400.7 (B) [ September 08, 2005, 07:43 PM: Message edited by: benaround ]
Re: drop cords from the ceiling. 406.4??????? 400.7 (B) [ September 08, 2005, 07:43 PM: Message edited by: benaround ]