Re: drop-in fixtures
First, thanks for all the great information. I have cruised this forum for a while picking up some really nice tidbits of very useful information.
Second, this is my first time posting so take it easy on me. I have read some threads and noticed some guys getting "jumped in" as if by a gang. If this post shows up in all caps, I didn't mean it I swear!
I wanted to add to the thread just a little as I have read several post about NM containing THHN/THWN conductors and the 90C rating of the cable. The UL standard (UL 719) for NM is pretty clear in paragraph 1.1 that both NM and NMC carry the "-B" marking. This indicates that today all NM cable be rated 90C as it is.
The standard also reads:
"6.1 Both before and after assembly into finished cable, the insulation employed on the circuit conductors shall comply with (a) or (b):
a)THHN Construction ? Jacketed insulation for a Type NM or NMC cable shall have a nylon or similar jacket and shall comply with the thickness and other applicable requirements for Type THHN thermoplastic-insulated wire without (see 25.18) any surface marking of ?THHN?, ?-B? or any ampacity or temperature rating.
b)TW Construction ? Insulation without a nylon jacket shall comply with the thickness requirements for a Type TW?
25.18 No conductor type letter designation and no current or temperature designation shall be included in the marking on the tag, reel, carton or directly on or in the cable."
As you can see all conductors in NM are THHN or TW. I think all companies actually supply THHN. Also you can see that it is not allowed in the standard to print the conductors with any marking such as "THHN/THWN". Therefore they are not allowed to be removed from the sheath and used as stand alone conductors for any location wet, dry, hot or cold.
This leaves the 90C rating for 2 reasons that I can think of. 1) Derating from the 90C column, but ampacities not to exceed 60C per 334.80. 2) Terminating in high temp fixtures.
Sorry for such a long post.