Steve L.

Member
Hi,

I was helping someone cut a tree down and it fell on the overhead triplex to the residence. The neutral wire was previously damaged and our branch severed it completely causing a T.V., flourescent light and a heating blanket to spark and burn out. I spoke with the power co. worker but did not fully understand his explanation. Can you help?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
All those loads became series loads on a 240 volt circuit and the higher resistance loads saw an elevation in voltage I x R = V

Using the above formula calculate the voltages on each of the lamps in the open neutral circuit below

lost_neutral_correct_copy(1).jpg


Roger
 
Last edited:

LawnGuyLandSparky

Senior Member
roger said:
All those loads became series loads on a 240 volt circuit and the higher resistance loads saw an elevation in voltage I x R = V

Using the above formula calculate the voltages on each of the lamps in the open neutral circuit below

lost_neutral_correct_copy(1).jpg


Roger

HOMEWORK? On FRIDAY? :wink:
 