I am being told that if the motor branch circuit calculation for TW wire comes out to 30.25 amps that I have to use #8 wire. I thought you could drop the .25 amp as per 220.2 B, and use #10. Also the same person tells me that you can use 220.2 B to drop small percentages of Kw when doing oven calculations. Can anyone confirm or correct these?