Installing a transformer (Dry type) indoors in an industrial/manufacturing facility. Reviewing NEC section 450.21(B) requires all dry transformers above 112.5 KVA installed indoors to be installed in a transformer room. This must be a fire resistant room with a 1 hour fire rating. There is an Exception to this section which will allow enclosed dry transformers (w/ventilating openings) to be installed without a transformer room if the insulation class is 155 or higher.
Does this insulation class refer to the temperature rating in degree C??