The grounding (bonding) conductor from a separately derived system (dry type transf. which has the GEC bonded to XO at the transf) to the panel (first disconnect) - isn't this a system bonding jumper (per 250.30 (A) (1) )? And as such shoudn't it be sized based on 250.28(D)?
I have looked through all my emails and your archives and found a picture from 'Grounding vs Bonding Online Training 18' that indicates the system bonding jumper from the XO to the grounding terminal attached to the transf, but it doesn't clarify from the transf to the panel. There may be another picture elsewhere but I have not found it.
What I have found and what I have been basing my belief on is the 1999 NEC Handbook, Figure 250.12A, that does show a "Main Bonding Jumper" from the transf to the first disconnect.
What do you think?
I have looked through all my emails and your archives and found a picture from 'Grounding vs Bonding Online Training 18' that indicates the system bonding jumper from the XO to the grounding terminal attached to the transf, but it doesn't clarify from the transf to the panel. There may be another picture elsewhere but I have not found it.