We designed a new construction project a while back and assumed a 208/3 service was available, turns out it is but it would cost $30,000 to go from 480/3 to 208/3 on the utility side (not sure why). The electrician drew a sketch for us with a 300 kVA dry type transformer being installed outside. The problem is that our load is only around 150 kVA and we could probably run some stuff on 480 which would reduce the required transformer size to maybe even 112.5 kVA. The reason why he wants to use a 300 KVA is because they have one they are trying to get rid of and can sell it to the owner really cheap. Does anyone see any problems with running a transformer at such low load conditions?
Chances are, this wont go ahead anyway because the sketch they drew did not have secondary over current protection. They were under the impression they could use the smaller 200A disconnects fed from the wire way that the transformer is feeding for secondary protection, essentially protecting the transformer with parallel disconnects. Once we show the secondary disconnect and feeders, they will probably change their mind.