Dry type Transformers versus Oil Filled

Status
Not open for further replies.

aelectricalman

Senior Member
Location
KY
We are looking into the differences between dry type and oil filled transformer and understand the benefits of both types (somewhat). In this particular situation we are stepping up 480Y/277 to 12470 for a photovoltaic system. The 800kVA to 1500kVA transformers will be outside in the weather on a concrete pad. At what point should I consider oil filled or it there always a dry type that will work. I was under the impression we will need to use an oil filled outside in 90 deg ambient temps due to the dry types inability to disapate heat. Does anyone have any thoughts? Is it always a requirement or good practice to use oil filled outside?
 
We are looking into the differences between dry type and oil filled transformer and understand the benefits of both types (somewhat). In this particular situation we are stepping up 480Y/277 to 12470 for a photovoltaic system. The 800kVA to 1500kVA transformers will be outside in the weather on a concrete pad. At what point should I consider oil filled or it there always a dry type that will work. I was under the impression we will need to use an oil filled outside in 90 deg ambient temps due to the dry types inability to disapate heat. Does anyone have any thoughts? Is it always a requirement or good practice to use oil filled outside?

Liquid filled transformers are cheaper and more efficient. They will also lasts longer as long as you monitor the condition of the insulating fluid. Consider high-flashpoint biodegradable fuel for reduced fire risk and nitrogen padding for life optimization.
 
I agree with what weressl posted, another option is cast coil, more expensive but the best of both (Dry and liquid) worlds.
 
Based on what?

As long as you don't care about:
[*]initial cost,
Yep, initial cost is more
[*]operating cost(efficiency), and
?? Opearting costs are minimal, they are essentially maintenence free, no cleaning (Dry) or oil analysis required. %Z is comparable (4-8%)
[*]BIL cost,
Cast coil BIL strength is superior to dry type and about the same as oil filled, BIL's of up to 200kV are available.
[*]service life.
Insurance company data shows cast coil failre rates are around 5% of standard dry types, expected service life is superior to dry type.

Cast coils are also:
- Moistyre proof
- Fire retardant
- Safe for environment, no toxic gasses or fluids can be emmitted to atmosphere
- Smaller footprint for limited space applications
-Higher overload capability than fry or oil
-PD free
-Superior short circuit capability to oil or dry
 
Last edited:
Based on what?

Yep, initial cost is more
?? Opearting costs are minimal, they are essentially maintenence free, no cleaning (Dry) or oil analysis required. %Z is comparable (4-8%) Cast coil BIL strength is superior to dry type and about the same as oil filled, BIL's of up to 200kV are available.
Insurance company data shows cast coil failre rates are around 5% of standard dry types, expected service life is superior to dry type.

Cast coils are also:
- Moistyre proof
- Fire retardant
- Safe for environment, no toxic gasses or fluids can be emmitted to atmosphere
- Smaller footprint for limited space applications
-Higher overload capability than fry or oil
-PD free
-Superior short circuit capability to oil or dry

The 150% premium can never be recovered unless you are paying 10 times the current electricity rates TODAY and inflation escalation will track with cost of power.
Cast coils still have exposed leads, still relies on atmospheric cooling - unless they are in a sealed, pressurized tank - therefore still exposed to the outside atmosphere which needs to be largely free of chemicals that may attack. Square D still talks about "ease of cleaning coil".
Efficiency still remains an issue. Of course they can build any efficiency you want, but at a cost.
If you install it indoors, heat removal and real estate cost still comes into the picture, but liquid filled does not have to be indoors and outdoor space is considerably less costly.
Non-toxic insulating liquids that are also high firepoint have Zero environmental impact. They fall into the same category as edible oils, just don't have FDA approval.:lol:
PD issue still remains valid for the primary and secondary leads and their entry point into the cast body is the weakest point.
Cast coils are also unrepairable.
 