Dryer and Range Cords
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Have I been unaware my entire life that range cords have always used different sizes. For instance a range cord can have 2- #6 and 2-#8 I assume the #8's are for neutral and ground. 40 amp Cords use #8 and #10 and obviously has a 50 amp end.
The ones I used to buy only stated range cord.
Dang, man. I have never looked. I hope you don't lose sleep over it.
Ron
There are enough things in life to lose sleep over. This isn't one of them. I assume this was a way 2 get what they wanting perhaps because some wire sizes were hard for them to get.
Same with 3-wire cords. I've known for a long time.
I'd have told you if I had known you didn't know. ;)
Most oven/ranges have less than 2 amps on the neutral. Computer/display, fans, oven lights, door locks for cleaning. The elements are mostly all 240vac. Some higher end models will cycle the C from element. NC to Netural and NO to Line2, which will switch the element wattage down 1/4 power. But those are few and far between.
The one at home depot does not state wire sizes
However this site does.
No one should be surprised if the manufacturer uses smaller conductors to save a few cents on each cord they make.
Yeah when I am pulling in pipe and wire, I will often use a 12 white for the neutral of a dryer. I probably would for a range too, although I don't think I've come across that scenario. I know there isn't an allowance in the code to reduce the neutral for the branch circuit to these, but I'm confident a busload of nuns will not die because of it
Edit. To be clear I would use a number 10 neutral for the range.
The neutral should not be smaller than the equipment grounding conductor. IMO, the #12 neutral for the 30 amp dryer is a violation
It's an interesting topic. I wonder if you looked at a 20 year old range cord if the conductors would all be the same size.
Yeah, I was thinking because the economy is where it is at and materials were hard to come by that they decided to cut corners to save some money. I wonder if that type cord is only made for dryer and ranges.
#12 is good for 30 amps
Of course that is not allowed due to terminal limitations. But an interesting question arises with the small conductor provision. Would that apply to a neutral conductor?
Imo, although I cannot back it up, the neutral must be the size of the equipment grounding conductor at least. This is true for neutrals in feeders and the same for the neutral in services in relation to the grounding electrode conductor.
Just splice it to 10 before termination ;) for terminal issue. Though 10 and under are limited to 240.4 d requirements