That is not the question to which you need an answer. I?ll tell you why in a moment.
The NEC requires you to use 5000 VA for a dryer, regardless of its nameplate rating. But it allows a 50% demand factor for 10 dryers. So if these will all go on the same feeder, then 10 times 5000 times 50% divided by 208 and divided again by 1.732 gives you about 70 amps.
The NEC requires at least one laundry circuit of 1500 VA under some circumstances. But that would not apply here. 220.53 says you can take the nameplate rating of the 10 washers and multiply by a demand factor of 75%. But you didn?t give us that nameplate rating. So you will have to do the math yourself.
But don?t bother with the math, or I should say don?t bother with the demand factors. I will guarantee you that these 10 washers and 10 dryers will all be running at the same time for a significant portion of their useful lifetimes. Using the NEC demand factors will give you a minimum installation, but not an acceptable installation. You need to go beyond the minimums, or else the owner will be talking to you about ?fixing? the problem of tripping breakers at your own expense. You might think you have the right side of the law on this one, but do you really want to undergo that discussion? Talk with the owner now, and make sure the owner knows why you need to go beyond the NEC minimums.